Hi guy,
was someone able to do polling data with Mitsubishi Q02UCPU through ethernet card QJ71E71-100 and eWON Flexy?
Any example to setup IOserver and PLC?

Thank you

regards

Marco
Reply

Jean-Yves Offline
eWON Support
#2
Hi,

After you set in the PLC the Port number, the networks number and the PC number it's 

CPU Type Adresse IP Port number Network Number PC Number MELSEC Ioserver
Q UDP 192.168.140.10 5000 1 5 QCPU,UDP,192.168.140.10,5000,1,5


.png   2018-06-21_09h42_57.png (Size: 6,73 KB / Downloads: 89)


.png   2018-06-21_09h43_26.png (Size: 15,92 KB / Downloads: 71)
Reply

Luca Mori Offline
Junior Member
#3
Hi Jean, 
Thanks to your answer we managed to solve the issue.

I'm not really into PLC in general, nevertheless  Mitsubishi PLC so, even if everything is working, I don't really get the meaning of this configuration.

Anyway, I would like to share a tips for anyone else that may find himself on the same spot.
Be aware of the checkbox that allow writing on the cpu .
While on the integrated Ethernet port it seams to be allowed by default, on the expansion card is the opposite.


Thanks again for your time
Reply

djonedd Offline
Junior Member
#4
(21-06-2018, 09:59 AM)Jean-Yves Wrote: Hi,

After you set in the PLC the Port number, the networks number and the PC number it's 

CPU Type Adresse IP Port number Network Number PC Number MELSEC Ioserver
Q UDP 192.168.140.10 5000 1 5 QCPU,UDP,192.168.140.10,5000,1,5
Hi Jean,

I have PLC Mitsubishi Q03UDVCPU, and it have built-in ethernet,
when i configure Melsec IOserver, i use parameter:  QCPU,UDP,192.168.0.10,5020,0,255    rate: 500ms
but the connection not stable, in status sometimes i got "2" (STATUS,QCPU,UDP,192.168.0.10,5020,0,255)
the topology: Flexy205 <-> ethernet switch <-> PLC
in the network i use for other device: HMI and Barcode Scanner (using MC Protocol, with different Port number)
Do you know how to solve it or make it stable?
And, do you know how i can found networks number and pc number in plc built-in ethernet?
Thank you,

Joned

 
Reply

Jean-Yves Offline
eWON Support
#5
It's normally here

[Image: attachment.php?aid=676]

0 and 255 are fixed

Careful regarding if it's HEX or DEC this depends on you Gxworks and the format is written in the message just below the table


Attached Files
.png   2020-04-02_14h06_08.png (Size: 143,7 KB / Downloads: 114)
Reply




Possibly Related Threads…
20-08-2025, 09:29 PM
Last Post: Kevin Zuñiga
04-08-2025, 05:43 AM
Last Post: djonedd
02-12-2024, 08:15 PM
Last Post: giallo
09-05-2024, 10:37 PM
Last Post: ricard0g0mes
02-02-2024, 02:04 PM
Last Post: Jean-Yves
22-12-2023, 03:30 PM
Last Post: simon
04-12-2023, 12:27 PM
Last Post: SamonC
02-11-2023, 10:51 AM
Last Post: espence
  CP1E OMRON POOLING DATA Started by djonedd
0 Replies - 1.344 Views
11-09-2023, 12:39 PM
Last Post: djonedd
02-09-2023, 11:42 AM
Last Post: RaulArait



Users browsing this thread:
1 Guest(s)



Theme © Ewon 2019 - Forum software by © MyBB - Cookie policy