19-06-2018, 05:47 PM (This post was last modified: 20-06-2018, 09:19 AM by spessi.)
Hi guy,
was someone able to do polling data with Mitsubishi Q02UCPU through ethernet card QJ71E71-100 and eWON Flexy?
Any example to setup IOserver and PLC?
Hi Jean,
Thanks to your answer we managed to solve the issue.
I'm not really into PLC in general, nevertheless Mitsubishi PLC so, even if everything is working, I don't really get the meaning of this configuration.
Anyway, I would like to share a tips for anyone else that may find himself on the same spot.
Be aware of the checkbox that allow writing on the cpu .
While on the integrated Ethernet port it seams to be allowed by default, on the expansion card is the opposite.
After you set in the PLC the Port number, the networks number and the PC number it's
CPU Type Adresse IP Port number Network Number PC Number MELSEC Ioserver
Q UDP 192.168.140.10 5000 1 5 QCPU,UDP,192.168.140.10,5000,1,5
Hi Jean,
I have PLC Mitsubishi Q03UDVCPU, and it have built-in ethernet,
when i configure Melsec IOserver, i use parameter: QCPU,UDP,192.168.0.10,5020,0,255 rate: 500ms but the connection not stable, in status sometimes i got "2" (STATUS,QCPU,UDP,192.168.0.10,5020,0,255)
the topology: Flexy205 <-> ethernet switch <-> PLC
in the network i use for other device: HMI and Barcode Scanner (using MC Protocol, with different Port number)
Do you know how to solve it or make it stable?
And, do you know how i can found networks number and pc number in plc built-in ethernet?
Thank you,