Queries between Flexy 205 with S7_1500 - Alvin - 07-08-2018

Hi ,

My client had a project link between Flexy205 with S7_1500.
Below attach is the IO server setting from my client.

Below is My client queries:
1.he would like to know the Called TSAP for S7-1500 can support ?
2.How to know the address such as M100.01 =?

Thank you,
Alvin


RE: Queries between Flexy 205 with S7_1500 - ziozetti - 22-08-2018

(07-08-2018, 10:46 AM)Alvin Wrote: Hi ,

My client had a project link between Flexy205 with S7_1500.
Below attach is the IO server setting from my client.

Below is My client queries:
1.he would like to know the Called TSAP for S7-1500 can support ?
2.How to know the address such as M100.01 =?

Thank you,
Alvin
Hi Alvin,
1. TSAP on my project is 03.01; I think it is always 03.01.
Remember! "It is important to release the access to the PLC. Therefore you need to go into the TIA Portal and release the “PUT/GET communication."
https://websupport.ewon.biz/support/product/s7-300-400-1200-1500-vipa/s7-300-s7-400-s7-1200-s7-1500-vipa
2. You should ask address table to the software engineering and/or check if there are addresses in the electric scheme.