Hi,

I have a Schneider PLC connected to my Ewon Flexy 205 via Modbus TCP communications. I want to be able to read the values of the PLC from the Modbus addresses. I noticed that the PLC programmer has given the Modbus addresses in a 6 digit format rather than a 5 digit format (eg 401112).

When I tried inputing a 6 digit number to the Ewon Flexy Setup (see attached picture)[attachment=1678], it will always go red. Is there a way I am able to read 6 digit modbus addresses? Or am I required to tell the PLC programmer to put the values all into 5 digit modbus addresses?

Thank you for your help.
Try with +401112
(19-09-2023, 01:07 PM)ziozetti Wrote: [ -> ]Try with +401112

Thank you very much for this! =)