Dear support,

I only want to send the process values (4 tags) of my Ewon Flexy's with Data management. Every 10 minutes.
For this I select only group A, and the tags process values I have named group A.

If I want to download the tag with the Ewon connector tool in Ignition SCADA, it still extracts all tags from the Flexy's.

It seems that the (de) selection of the other tags does not happen.

Can you please help me with this problem?

Firmware: 14.0s02 (#1005)

[font="Open Sans", "Helvetica Neue", helvetica, arial, verdana, sans-serif]Firmware: 14.0s02 (#1005)[/font]
Hi,

This behavior is actually normal.
The Tag group allows to filter the Tag Historical Data but not the Tag definition.
So, in other words, all Tags are always sent in the Tag definition (var_lst) but only the group A tags are sending their histo data (binary file)

Simon
One thing you can try is to double-check the configuration of the Ewon connector tool to ensure that it is set up to only download the process values for group A. You may also want to check the settings on the Ewon Flexy to ensure that the tags you want to download are properly configured and enabled for group A.

Another step you can take is to check the settings on the Ewon Flexy itself. Ensure that the tags you want to download are correctly configured and enabled for group A. This may involve adjusting the settings on the Flexy or updating the configuration files to ensure that the correct data is being downloaded.

In summary, to ensure that the Ewon connector tool downloads the correct process values for group A, it's important to double-check the configuration settings and verify that the appropriate tags are enabled for download. By taking these steps, you can help ensure that you are doing accurate lead data enrichment from your Ewon Flexy.